查看: 1921|回复: 2
收起左侧

[标准类] 变频电缆填料函

[复制链接]
发表于 2022-11-27 11:58 | 显示全部楼层 |阅读模式 来自: 中国江苏泰州
哪位大神晓得变频电缆进接线箱或者进泵对电缆填料函有没有要求,请高人指点
回复

使用道具 举报

龙船学院
发表于 2022-11-28 08:07 | 显示全部楼层 来自: 中国山东烟台
1. VFD cable earthing in converter side: use EMC screen clip or useful steel strip to create a solid 360° contact between the shield and EMC screen bus bar. The armor should be made into a pigtail and connected to PE bus as well as the three grounding cores.
2. VFD cable earthing in motor side: cable should be taken off the insulation after going into the motor box and the screen and armor should screwed  into a pigtail together, this pigtail should connect to PE bar as well as 3 grounding cores. The installation must be sure that interference current can find a continuous, low-inductance path without interruptions or weak points throughout the shield between motor and converter or it is far less             effective in preventing interference currents from spreading beyond the drive system.
回复 支持 反对

使用道具 举报

发表于 2022-11-28 08:08 | 显示全部楼层 来自: 中国山东烟台
最好选用EMC CABLE GLAND,有的OWNER会要求。
回复 支持 反对

使用道具 举报

您需要登录后才可以回帖 登录 | 立即注册

本版积分规则

小黑屋|标签|免责声明|龙船社区

GMT+8, 2024-9-28 01:51

Powered by Imarine

Copyright © 2006, 龙船社区

快速回复 返回顶部 返回列表