1. VFD cable earthing in converter side: use EMC screen clip or useful steel strip to create a solid 360° contact between the shield and EMC screen bus bar. The armor should be made into a pigtail and connected to PE bus as well as the three grounding cores.
2. VFD cable earthing in motor side: cable should be taken off the insulation after going into the motor box and the screen and armor should screwed into a pigtail together, this pigtail should connect to PE bar as well as 3 grounding cores. The installation must be sure that interference current can find a continuous, low-inductance path without interruptions or weak points throughout the shield between motor and converter or it is far less effective in preventing interference currents from spreading beyond the drive system.
|
|