发表于 2017-2-28 10:43
|
显示全部楼层
来自: 中国浙江舟山
以前做的BV RINA的一人桥楼(SYS-NEQ1)里面也类似要求,是关于Alarm transfer system的:RINA PART F CH4 SEC 1(SYS-NEQ):
6.3 Alarm/warning transfer system - Communications
6.3.1 Any alarm/warning that requires bridge operator response is to be automatically transferred to the Master and, if he deems it necessary, to the selected backup navigator and to the public rooms, if not acknowledged on the bridge within 30 seconds.
我们以前是通过上海RAYE航海报警来实现这个功能。把一些重要报警比如偏航、碰撞、水深等等做到航海报警里面。如果任一报警30S不复位就激活后备官员的蜂鸣器。为了不打扰所有后备官员我们也另外设置了一个后备官员选择开关。
对于ALARM TRANSFER SYSTEM在ISO8468也找到了,不过功能就是BNWAS的EM'CY CALL,所以想是不是航海报警30S不复位就触发BNWAS的EM'CY CALL。
ISO8468 :
5.5.3.2 Alarm transfer system
Means may be provided on the bridge to immediately activate a second, and subsequently third, stage remote
audible alarms by means of an .Emergency Call. push button or similar.
Acknowledgement and cancellation of alarms shall only be possible from fixed locations on the bridge.
|
|